Author Topic: internal insulation of solid masonry walls revisited  (Read 25243 times)

peter smithdale

  • AECBmember
  • Posts: 17
    • View Profile
internal insulation of solid masonry walls revisited
« on: May 08, 2008, 10:22:53 AM »
It seems to me that internal insulation systems of any type are risky because you get a dewpoint on the inside face of the masonry. We rely on the moisture drying out internally or externally, eventually, and causing no harm in the weeks or months it sits there. However there is a risk (in my view) that particularly wet, poorly ventilated, or cold (internally or externally) parts of a building may never dry out as well as hoped and a permanent build-up of moisture may result. This may be the result of peculiar outdoor conditions, occupant behaviour or failed ventilation.

In short, the systems lack robustness, particularly those that rely on vapour control layers - as a robust system would survive the occasional gap caused by poor workmanship or alterations to the building in later years.

I know one needs to really understand the moisture sinks, orientation, prevailing weather and occupant behaviour in a building, to understand how well it would dry out before and after insulation. My fear is that this understanding would put the careful building owner off insulating completely. Certainly as a specifier this has happened with me.

The condensation risk calcs are far too crude a measure as they do not factor in these conditions.

The main issue seems to be enhancing the vapour permeability of the masonry so that vapour can escape to the outside more easily. Or even full-blown ventilation like a 'traditional' cavity wall.

Draining the 'bottom' of such a 'cavity' is clearly a big technical problem but enhancing the drying would be a step in the right direction. I'm wondering if holes, plugged with something breathable (to allow vapour out but stop the wind and rain howling in), through the masonry might be a good idea. I'm aware that lime mortar joints do this job but most masonry walling I come across is rebuilt or repointed with less permeable mortar. Perhaps holes at certain centres through the joints, plugged with lime mortar.

I expect someone has thought of this before. It reminds me of the ceramic tubes that are / were used to dry walls out.

Comments anyone?

fostertom

  • AECBmember
  • Posts: 400
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #1 on: May 08, 2008, 01:11:45 PM »
What about something like min 75 of Hemcrete sprayed integral (no voids) onto the bare-masonry inside face of the wall? More or less robust?

Nick Grant

  • Moderator
  • Posts: 1312
    • View Profile
    • Elemental Solutions
Re: internal insulation of solid masonry walls revisited
« Reply #2 on: May 13, 2008, 06:56:50 AM »
Peter I have reached the same conclusion and lack confidence recommending internal insulation unless the building is a shell and a new box can be built inside!

On one hand the insulation needs some vapour resistance but some systems rely on the drying out happening into the room.

One of my main concerns is joist ends penetrating the insulation layer and sat in a wall.

Having said all this I know builders who have been dry lining for years and claim never to have had a problem. Perhaps I am over pessimistic? Perhaps the plasterboard is holding the dry, solid end of the floor joists??

Keen to hear experience of people who have been more daring than me.
« Last Edit: May 14, 2008, 08:16:50 AM by Nick Grant »

Mark Siddall

  • Moderator
  • Posts: 1222
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #3 on: May 13, 2008, 10:33:00 AM »
For an interesting take on internal insulation and the tricky floor details have a look at "Canadian Refurb Methodology" on this thread
http://www.aecb.net/forum/index.php?topic=1210.msg4933

The spraying an airtight insulating foam directly to the back of the external leaf seems to be a "done thing" is low energy circles in the USA. This technique is being used on a new build PH at Marthas Vinyard in the USA (Marc Rosenbaum recomended the approach in the first instance, I think as a means of achieving airtightness.... I can't remember).

Mark
« Last Edit: May 13, 2008, 05:58:36 PM by Mark Siddall »

Mark Siddall

  • Moderator
  • Posts: 1222
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #4 on: May 13, 2008, 06:22:10 PM »
Thinking about the Canadian/American "flash foam" solution above a little more: -

The concern is often raise that the floor joist could fail structurally due interstitial condensation and subsequent rot. The flash foam method of feathering the insulation so that it is thinner in this location helps to raise the temperature within the wall. The ultimate aim of the game would be to ensure that the end of the joist stays above the dew point. In terms of design, when assessing the viability of the detail, some 3D thermal bridge analysis (using TRISCO, HEAT3 or similar) would be ideal to determine the appropriate insulation level under design conditions.

Anyone willing to give it a go? (Does anyone have TRISCO or HEAT3?)

Mark


peter smithdale

  • AECBmember
  • Posts: 17
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #5 on: May 14, 2008, 12:28:31 PM »
The document on the Canadian link is the most advanced thinking I have seen so far on this, thanks for highlighting it.

The idea of metal wedges conducting heat into the joist ends is intriguing.

I spoke to British Gypsum technical and they admitted that any air leakage behind thermal plasterboard laminate would likely lead to condensation in the cavity. Achieving a perfect long-term seal does seem optimistic in the extreme.

Another thought (and it is just a thought) as thermal laminate linings typically stop at the ceiling and floor at an intermediate floor, it could be argued that the situation of the floor edge and joist ends is little different to it was before insulation, except the building is probably better heated. They only affect the bit of wall immediately behind themselves. This is a cold surface where condensation is likely, but that would be the case if the room was uninsulated.


gerald smith

  • *
  • Posts: 2
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #6 on: January 15, 2009, 03:50:38 PM »
I am just a poor soul who owns a dampish, stone-walled dwelling that badly needs wall insulation as part of refurbishment now being planned. I have no direct experience of/professional training in the options BUT - having read and read, talked and talked I am moved to give the Canadian approach a go, even after digesting the very good and helpful "old stone buildings" literature. The unknowns would seem to be that damp Welsh winters versus dry Canadian ones may:-
1) cause more condensation within walls/on internal surfaces
2) not be vapour open enough to allow sufficient internal evaporation
3) be a greater risk to old timbers set into walls

Would any of you like to specify and price a Canadian system for part (I don't want the whole building to collapse or have to be cored out around me!) of the above dwelling to include long term temperature and moisture monitoring and publication of the results on this site??? "Just doing it" does not seem a truly safe thing to do. An experiment properly set up does.
 

jon day

  • *
  • Posts: 8
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #7 on: February 07, 2009, 04:07:12 PM »
Peter, there is a EN standard of how the dewpoint of a wall should be calculated. the old standard did not recognise drylining as a legal method in europe, except for THE rare occasions were there was (a high capital expenditure !). The old standard has been replaced by a new one and it would be interesting to see if it will be put into british legislation?

through out europe the preferred method of insulating buildings is externally. this is done for a huge variety of reasons not just for the manufacturer.

if you insulate internally the dewpoint is brought nearer to the inside of the wall. which will still allow condensation to occur. which then allows all other serious problems to occur.

Jon


Mark Siddall

  • Moderator
  • Posts: 1222
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #8 on: February 08, 2009, 02:30:13 PM »
Jon,
To which EN standards do you refer? ("Old" and "New")

Are you refering to BS EN ISO 13788: 2002 (Hygrothermal performance of building components and building elements Internal surface temperature to avoid critical surface humidity and interstitial condensation Calculation methods)? Are you suggesting that this has now been superceeded?

Cheers,
Mark

jon day

  • *
  • Posts: 8
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #9 on: February 14, 2009, 05:47:31 PM »
Hi Mark

Yes the EN standard iso 13788:2002 has been superceded. It has been replaced by EN 15826:2007

May i complement all at the AECB for there determination and hard work into bringing the Passivhaus Standards and ideals to the forefront in the Uk.These are exciting times ahead. Its been long over due.
Keep up the good work.

Cheers
jon

« Last Edit: February 14, 2009, 07:04:26 PM by jon day »

Stuart Evans

  • *
  • Posts: 1
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #10 on: June 08, 2009, 04:09:55 PM »
Hi
This is the first time I have posted anything on this forum and have found the replies to this topic very interesting, however I am still unsure of the best solution for internally insulating solid masonry walls.
We are involved in an extensive refurbishment of a grade 2 listed victorian lodge near York. As part of the refurbishment we are intending to internally insulate all external walls.
Our proposal was to use either timber studs or a metal frame system to line out the walls with K18 Kingspan insulation boards with integral plasterboard. The local conservation officer has rejected this detail citing that we are not dealing with the risk of interstitial condensation building up within the masonry and not allowing the existing wall to 'breath'. His suggestion was to use hygrocopic materials -Sheep's wool insulation and timber lath and traditional plaster. After reading this forum I beleive that his alternate method could actually cause an increase in moisture build up on the internal face of  the existing wall. is this correct?

I suggested a hybrid solution using timber studs with sheeps wool packed tight between studs and to wall face with new 12.5 p/board face. His reply was that p/board won't allow the wall to breath???? and that lath & plaster should be used. This lead me to believe his agenda was more about using traditional materials rather than the correct insulating detail.

Has anyone come across a similar problem? Can anyone advise me what is the best solution?

Thanks




niall crosson

  • AECBmember
  • Posts: 11
    • View Profile
    • Ecological Building Systems
Re: internal insulation of solid masonry walls revisited
« Reply #11 on: June 16, 2009, 11:54:11 PM »
Hi Stuart,

Approaching these types of walls from the inside is always quite difficult. We have examined various alternitives for such a wall ranging from woodfibre, to hemp to sheepwool, and cellulose. A calium silcate board (e.g. Calsitherm), provides the most robust solution in these cases. These boards have an exceptional vapour absorption property, insulate and are extremely resistant to mould growth. They are often used in the refurbishment of historic buildings in Germany.

Cheers,

niall

Peter Bayer

  • AECBmember
  • Posts: 75
    • View Profile
Re: internal insulation of solid masonry walls revisited
« Reply #12 on: June 19, 2009, 07:07:27 PM »
Niall

Could you point me in the direction of some information on using calcium silicate insulation in this application, all I've found so far is pipe lagging for chemical plants and refractory linings .

thanks

Peter
« Last Edit: June 22, 2009, 11:07:46 AM by Peter Bayer »

niall crosson

  • AECBmember
  • Posts: 11
    • View Profile
    • Ecological Building Systems
Re: internal insulation of solid masonry walls revisited
« Reply #13 on: June 19, 2009, 07:51:40 PM »
Hi Peter,

You can get some info on www.klimaplatte.de
I'm afraid its only in german but the videos showing application are pretty good. I have  a pdf from them in english which i can mail you if wish but maybe your german is better than mine;)
Niall

 