    Thanks Mark,

    Thinking about it more carefully, we have quite deep joists (175mm), and a friendly spray foam contractor.

    In a warm roof, the thermal resistance of the between rafter insulation must not exceed the thermal resistance of the over rafter insulation layer, so:

    100mm of Kingspan K7 phenolic insulation above the rafters: lambda = 0.020 (90/90), r= 5.00
    150mm of Lapolla FL2000 closed cell PU spray foam between the rafters: lambda = 0.030, r =5.00
    U=0.116 (PHPP, 20% timber in the foam layer) Foam density 30kgm3 Mass 4.5kgm2

    90mm of Kingspan K7 phenolic insulation above the rafters: lambda = 0.020 (90/90), r= 4.50
    130mm of Lapolla FL2000 closed cell PU spray foam between the rafters: lambda = 0.030, r =4.33
    U=0.130 (PHPP, 20% timber in the foam layer) Foam density 30kgm3 Mass 3.9kgm2

    I wonder whether to believe claims that closed cell PU foam can act as a vapour control layer and air barrier…